| Product(s): | STAAD Advanced Concrete Design | ||
| Version(s): | Connect Edition | ||
| Environment: | |||
| Area: | Concrete Design | ||
| Subarea: | Beam Design | ||
| Original Author: | Aaradhya Rahate, Bentley Technical Support Group | ||
How the effective depth is calculated in beam design and what is the impact of “maximum Aggregate 2 Size” on effective depth?
Reply:
RCDC assumes the number of rebars layers for the effective depth calculation based on the following,
Assumption of number of layers of reinforcement:
At design time the number of layers of reinforcement is assumed as under to arrive at the effective depth, d:
D < 400 mm 1 layer
400 mm >= D <=1200 mm 2 layers
1200mm > D <= 1350 mm 3 layers
1350 mm > D <= 1800 mm 4 layers
1800 mm > D <= 2250 mm 5 layers
2250 mm > D <= 2700 mm 6 layers
2700 mm > D <= 3250 mm 7 layers
D > 3250 mm 8 layers
Effective depth is calculated as follows,
Example-1
Beam Depth (D) = 600 mm
Clear cover (Cc) = 25 mm (this includes diameter of link/stirrups/fitment)
Maximum Aggregate 2 Size (M) = 25 mm
Assumed Diameter (d1) = 20 mm
Number of layers = 2 Nos (for 400 mm >= D <=1200 mm)
Space between two rebars (S) = if -- d1 > 2 * M / 3
Then d1 is considered
Else, 2 * M / 3 is considered
In the example considered,
20 > 2*25/3
20 > 16.67mm
Thus, spacing (S) between rebars is 20mm.
Effective depth = D – Cc - d1 – S/2
= 600 – 25 – 20 – 20/2
= 545 mm
Example-2
Maximum Aggregate 2 Size (M) = 40 mm
Number of layers = 2 Nos.
Space between two rebars (S) = if --- d1 < 2 * M / 3
Then d1
Else, 2 * M / 3
20 < 2*40/3
20 < 26.67mm
Thus, space (S) between rebars is 26.67 mm
= 600 – 25 – 20 – 26.67/2
= 541.665 mm
Thus, if user expects clear spacing between rebars to be 25mm, it is recommended user to provide value of Maximum Aggregate 2 Size (M) equal to 37.5mm. (2 x 37.5 / 3 = 25mm)
You may also refer the attached excel sheet for quick check.
communities.bentley.com/.../Deff-and-Ast-calculation.xlsx