| Version(s): | All | ||
| Subarea: | Loading | ||
| Original Author: | Abhisek Mandal, Bentley technical Support Group | ||
When does one use FLOOR LOAD and when does one use ELEMENT LOAD?
When modelling a grid system made up of horizontal beams and the slabs which span between the beams, we have found that there are 2 approaches that users take :
1) They model the beams only, and do not include the slabs in the model. However, they take into account the large inplane stiffness of the slab by using the master-slave relationship to tie together the nodes of the deck so that a rigid diaphragm effect is simulated for the horizontal plane at the slab level.
2) They model the slabs along with the beams. The slabs are modelled using plate elements.
The question that arises is, how does one account for the distributed loading (load per area of floor) which is present on top of the slab?
If you model the structure using method (1), the load can be assumed to be transferred directly on to the beams. The slab-beam grillage is assumed to be made up of a number of panels, similar to the squares of a chess board. The load on each panel is then tranferred to beams surrounding the panel, using a triangular or trapezoidal load distribution method. You can do this in STAAD by defining the load intensity in the FLOOR LOAD command. In other words, the pressure load on the slabs (which are not included in the model) are converted to individual beam loads by utilizing the FLOOR LOAD facility.
In method (2), the fact that the slab is part of the model makes it very easy to handle the load. The load can be applied on individual elements using the ELEMENT LOAD facility. The connectivity between the beams and elements ensures that the load will flow from the plates to the beams through the columns to the supports.