STAAD.Pro 22.02.00.26
List of critical and high severity defects identified in STAAD.Pro V22 build 22.02.00.26
Issue ID Title Severity 1st affected Build Fixed in Build
254014 Error in deflection check calculation in all design codes 2 - High 20.07.00.01 22.03.00.28
255402 Wind Load on Double angle section 2 - High 20.07.00.01 22.03.00.28
1013172 ACI 318-2014 - Mismatch in designed member number. 2 - High 21.00.02.30 22.03.00.28
1019936 Interaction ratio reporting error -IS 456 2 - High 20.07.00.01 22.03.00.28
1022412 Wind Load: Difference in wind load generation with different input unit 2 - High 20.07.00.01 22.05.00.131
1022413 Earthquake workflow - Metric vs English 2 - High 20.07.00.01 22.05.00.131
1022471 ASCE 10-97 code check reports incorrect Tensile Capacity 2 - High 20.07.00.01 22.04.00.40
1024768 Plate/Strips sections from the Dutch database are not designed by EN1993-1-1:2005 code 2 - High 20.07.00.01 22.03.00.28
1049980 For calculating Bending Leg local buckling capacity for Unequal Angles as per AISC 360-10, the software is using length of the smaller leg as b  2 - High 20.07.11.50 22.03.00.28
1050840 Pure torsion shear stress as per DG-9 is reported as zero for the AISC 360-05 code  2 - High 20.07.10.64 22.03.00.28
1052124 Pure flexure shear stress is incorrectly calculated for angles designed as per AISC 360-05 and AISC 360-10 design codes, as a part of DG9 code check. 2 - High 20.07.10.64 22.03.00.28
1052941 Concentrated member moment incorrect results diagram 2 - High 21.00.02.44 22.03.00.28
1057199 The Cy value input for the User table Tee sections are not used by STAAD.Pro when designing as per the AISC 360-16 code 2 - High 21.00.02.44 22.03.00.28
1058176 Models once edited in Editor and saved, the previous post-processing results are still available for viewing. 2 - High 22.02.00.26 22.03.00.28
1058631 AIJ 2002 and 2005 - Calculates incorrect Zx values for UPT-General section 2 - High 21.00.02.44 22.03.00.28
1058714 Wind Load Generation failing to load structure properly  2 - High 20.07.04.12 22.04.00.40
1059225 Incorrect static wind loading as per Russian 2016 wind load code for Building Structures 2 - High 21.00.02.44 22.03.00.28
1059242 Russian static wind load exposure factor issue for SP 20 2016 2 - High 21.00.02.44 22.03.00.28
1061506 Russian steel 2011 code issues 2 - High 20.07.11.50 22.03.00.28
1061951 Russian wind 2016 static load effective height ze. 2 - High 21.00.02.44 22.03.00.28
1062460 AIJ 2002 and 2005 - Incorrect Ix value used for UPT I section 2 - High 21.00.02.44 22.03.00.28
1062461 AIJ 2002 and 2005 - Calculates Incorrect Zx values for UPT Wide Flange Section 2 - High 21.00.02.44 22.03.00.28
1062471 AIJ 2002 and 2005 - Calculates Incorrect Bending Stress, Zy and Iw for UPT Channel Section 2 - High 21.00.02.44 22.03.00.28
1062537 AIJ 2002 and 2005 - Incorrect design results for UPT Tee Section 2 - High 21.00.02.44 22.03.00.28
1062566 AIJ 2002 and 2005 - Incorrect design results for UPT Asymmetrical Wide Flange Section 2 - High 21.00.02.44 22.03.00.28
1063041 IS800-2007 Bending capacity error for unsymmetrical sections 2 - High 21.00.02.44 22.03.00.28
1065829 Member Section Forces MX incorrect when concentrated moment applied to member. 2 - High 21.00.00.57 22.03.00.28
1067696 AIJ 2002 and 2005 - Tension Member Issue 2 - High 21.00.02.44 22.03.00.28
1067883 SNiP 1985 issues - Incorrect static wind load & OBLIQUE parameter 2 - High 20.07.04.12 22.03.00.28
1068121 Infinity unity ratio reported when tapered Square or I are designed as per AISC 360-16. 2 - High 21.00.02.44 22.03.00.28
1068762 Check Code All results for Deflection Check for AISC 360-16 Code are erroneous. 2 - High 21.00.02.44 22.03.00.28
1069722 Width to Thickness Ratio for Pipe Section as per AIJ 2 - High 21.03.00.146 22.04.00.40
1070791 Member Design results are changing when the model is reanalysed and members designed with IS:801 2 - High 22.01.00.39 22.04.00.40
1070794 Implement a warning saying that design of Class-4 built up sections is not supported by EN 1993-1-1:2005 code 2 - High 20.07.10.64 22.04.00.40
1071967 Incorrect Stress Reporting as per DG-9 when member is designed as per AISC 360 05/10 code 2 - High 22.01.00.39 22.04.00.40
1072277 AIJ 2002 and 2005 - Calculates incorrect Iw values for Wide Flange UPT section 2 - High 21.03.00.146 22.04.00.40
1072280 AIJ 2002 and 2005 - Calculates incorrect Zy and Iw values for UPT Channel section 2 - High 21.03.00.146 22.04.00.40
1072281 AIJ 2002 and 2005 - Calculates incorrect Zz values for UPT Tee section 2 - High 21.03.00.146 22.04.00.40
1074071 Variable pressure load applied in the physical model is being incorrectly applied in the analytical model 2 - High 22.02.00.26 22.04.00.40
1074884 AISC 360-16 reports incorrect deflection check results 2 - High 21.00.02.44 22.05.00.131
1075459 Incorrect web class being reported for a tapered member designed using IS: 800-2007 2 - High 20.07.11.50 22.04.00.40
1077199 Improper implementation of the Clause 6.1.4 of IS:13920-2016 for the code checking of Beam Members. 2 - High 21.03.00.146 22.04.00.40
1080055 Incorrect Moment capacity calculation as per AS4100-1998 2 - High 20.07.11.90 22.05.00.131
1081390 Analysis fails to get cold-formed section property data name includes W 2 - High 21.00.02.44 22.04.00.40
1081492 Incorrect Tensile Member Design as per AS4100-1998. 2 - High 20.07.11.90 22.05.00.131
1083183 AISC 360-16 - LTB design of single angles about the principal axis. 1 - Critical 21.00.02.30 22.04.00.40
1085903 Beams having side face reinforcements – fail in design as per ACI 318-14 2 - High 21.00.02.44 22.05.00.131
1085969 US Coldformed Channel with Lips sections added by user takes wrong properties 2 - High 20.07.04.12 22.04.00.40
1086128 Incorrect Section Property Values in Chinese Section Database in STAAD.Pro 2 - High 22.02.00.26 22.04.00.40
1086171 Error in LTB Check as per Canadian S16-14 Code 1 - Critical 20.07.11.33 22.04.00.40
1087315 Incorrect Joint Check as per IS13920: 2016 2 - High 22.02.00.26 22.05.00.131
1087329 IS13920: 2016 - Joint check having failed members connected to it 2 - High 22.02.00.26 22.05.00.131
1088695 Incorrect location is taken for some members when cl. 6.2.1(7) of EN 1993-1-1:2005 is checked 2 - High 20.07.10.41 22.05.00.131
1088980 IS:456-2000 - Beam Design - Moment corresponding to SFACE and EFACE command is not correct 2 - High 20.07.11.45 22.05.00.131
1089020 HSS Torsional Constant (C) of the PIPE section are incorrect in the Chinese section database 2 - High 22.02.00.26 22.04.00.40
1089913 US Coldformed Angle, AngleS, Zee, ZeeS, Hat and Pipe Sections added by user takes wrong properties 2 - High 20.07.04.12 22.05.00.131
1090036 Mass is not calculated correctly when floor diaphragm is assigned to nodes 2 - High 20.07.08.22 22.05.00.131
1092819 EC3: Incorrect Effective Length value for torsion and Total Torsion for Design are considered for code checking 2 - High 20.07.07.32 22.05.00.131
1092854 EC3: Incorrect design of members while checking for the Cl.EC-6.2.1(7) if ELB 1 is specified 2 - High 20.07.04.12 22.05.00.131
1093056 Unit conversion issue with IS:1893-2016 seismic parameter from Physical to Analytical mode. 2 - High 22.01.00.39 22.05.00.131
1093383 Incorrect Bending Capacity reported for Single Angle as per Canadian Steel Design Code 1 - Critical 20.07.11.33 22.05.00.131
1094012 Incorrect axial compression capacity being calculated as per IS 800 2007 (LSD) 2 - High 20.07.06.23 22.05.00.131
1094895 Adds MASTER NODE to diaphragm created in Physical modeler 2 - High 21.00.00.57 22.05.00.131
1095083 EC3: Incorrect calculation of 'c' for the depth to thickness ratio of Tee section for the section classification in EN 1993-1-1:2005 2 - High 20.07.04.12 22.05.00.131
1097343 Calculation of Effective Slenderness ratio as per Section E5 is ignored for Single Angle Sections for AISC 360-2016 Code. 2 - High 21.00.02.44 22.05.00.131
1098559 Program reports zero capacities for small load values using CSA S16-01 code 2 - High 20.07.04.12 22.05.00.131
1099476 Incorrect Centre of Rigidity calculation when Rigid diaphragm is defined using JOINT option 2 - High 21.03.00.146 22.05.00.131
1100275 Advanced Cable Analysis - Error in the Section displacements - Y direction 2 - High 20.07.11.50 22.05.00.131
1100975 Slenderness failure is considered incorrectly in AISC 360-10 and 360-05 Codes 2 - High 20.07.09.31 22.05.00.131
1101622 Incorrect Cw Calculation for members with general UPT sections and/or any I-shaped sections for AISC 360-16 design 2 - High 21.00.02.44 22.05.00.131
1101961 Slenderness failure is considered incorrectly in NZS3404-1997 2 - High 21.00.00.57 22.05.00.131
1101995 Slenderness failure is considered incorrectly in CSA S16-14 & S16-09 codes 2 - High 20.07.11.33 22.05.00.131
1103365 Incorrect Section Strength calculation for Semi-Compact section - IS 800 2007 LSD 2 - High 20.07.11.33 22.05.00.131
1103377 Incorrect section strength calculation for tapered I-section as per IS 800 2007 2 - High 20.07.11.70 22.05.00.131
1103936 Incorrect effective property calculation for Z-section with lips as per IS 801 2 - High 22.01.00.39 22.05.00.131
1103955 Incorrect Design forces considered for symmetrical sections in IS 800-2007 LSD design 2 - High 20.07.11.70 22.05.00.131
1106275 Incorrect base Shear calculation for Colombian Seismic code NSR-10 2 - High 20.07.10.41 22.05.00.131
1107006 Incorrect moment capacity for CLASS 4 Tee section per EC3 code 2 - High 20.07.04.12 22.05.00.131
1110683 Elastic section modulus is incorrectly calculated for I section with cover plates for AISC ASD (9th Edition) design 1 - Critical 20.07.11.90 22.05.00.131
1110726 Incorrect section modulus of wide flange with different sized Top & Bottom plates 2 - High 20.07.10.41 22.05.00.131
A-487590 Nonlinear Analysis - plate results reported as zero for model with multiple load cases 2 - High 22.01.00.39 22.06.00.138
A-487670 Incorrect base shear being generated as per Equivalent Lateral Force Method using IBC 2018 2 - High 22.02.00.26 22.10.00.153
A-487732 Incorrect Warping Constant used during selection of wide flange profiles as per AISC 360-16 2 - High 21.00.02.44 22.07.00.160
A-487738 Incorrect design as per AS4100 for a braced physical member having analytical node at any quarter point along its length 2 - High 21.00.02.44 22.06.00.138
A-487742 Error in torsion design for beams per ACI 318-2011 2 - High 20.07.11.50 22.06.00.138
A-505266 Incorrect Warping Constant used during selection of wide flange profiles as per CAN/CSA-S16-14 or CAN/CSA-S16-09 2 - High 21.00.02.30 22.06.00.138
A-506489 Incorrect Warping Constant used during selection of wide flange profiles as per IS 800 2007 (LSD/ WSD) 2 - High 21.00.02.30 22.06.00.138
A-511125 Incorrect Warping Constant used during selection of Channel profiles as per EN 1993-1-1 2005 or BS EN 1993-1-1 2005 2 - High 20.07.11.70 22.07.00.160
A-515693 Member assigned with MEMBER TENSION and subjected to axial tension - is designed as a compression member with NZS3404-1997 code 2 - High 21.00.00.57 22.06.00.138
A-524650 Member section displacement results do not account for lateral releases on members 2 - High 20.07.04.12 Known Issue
A-533716 The horizontal seismic influence coefficient (ALPHA) is incorrect for period from 0.1s to Tg as per GB50011-2001 2 - High 20.07.06.23 22.06.00.138
A-547383 IS801 compression capacity check for multiple properties 2 - High 22.01.00.39 22.06.00.138
A-554981 NZS 3404:1997 slenderness for tension members 2 - High 21.00.00.57 22.07.00.160
A-633034 NZS 3404-1997 : Clause 5.12.2 2 - High 21.00.00.57 22.07.00.160
A-669073 AISC 360-16: Warping constant is used in the calculation of Euler Buckling Stress for T & 2L Sections 2 - High 21.00.02.44 22.08.00.175
A-698135 SANS 10162-1 : UNT and UNB parameters 2 - High 20.07.11.33 22.09.00.115
A-710597 EN 1993-1-1: 2005 : Utilization ratio as per Eq.6.62 for Slender Tee section 2 - High 20.07.07.19 22.08.00.175
A-716046 EN 1993-1-1: 2005 : Shift of neutral axis for Slender Tee section 2 - High 20.07.07.19 22.08.00.175
A-774908 AISC 360-16: Effect of eccentricity for single angle profiles 2 - High 22.02.00.26 22.09.00.115
A-784278 AISC N690 1984: Shear design for pipe sections 2 - High 20.07.06.23 22.09.00.115
A-813848 Unbraced length : UNF and UNL Parameters 2 - High 20.07.08.32 22.10.00.153
A-817499 EN 1993-1-1:2005 : LEG parameter for single angle profiles 2 - High 20.07.07.32 22.11.00.156
A-852094 AISC 360-16 : FY and FU not considered from assigned material 2 - High 21.00.02.44 22.10.00.180
A-865805 Incorrect ELFP Torsional Moment : Optional Load Factor Multiplication 2 - High 22.01.00.39 22.10.00.180
A-865842 AISC 341-16 : Incorrect Seismic Classification for Custom Steel 2 - High 22.01.00.39 22.10.00.180
A-935629 AISC 360-16: SGR parameter 2 - High 21.00.02.44 22.12.00.142
A-969825 AISC 360-10/05 : Combined flexure and tension 2 - High 20.07.11.50 22.12.00.142
A-973697 AS4100-1998 : Moment modification factor 2 - High 20.07.11.90 23.00.00.345
A-1003677 NZS-3404-1997 : Physical member design 2 - High 21.00.00.57 23.00.00.345
A-1005695 NZS-3404-1997 : Analytical Member Design 2 - High 21.00.00.57 23.00.00.345
A-1032348 AISC 360-16 and BS5950 Pt 1 : Incorrect shear capacity parallel to the flanges for Double Channel profiles  2 - High 21.00.02.30 23.00.00.345
A-999611 Incorrect Time History analysis results with a Harmonic Ground motion  2 - High 20.07.04.12 22.12.00.142
A-1073141 IBC 2012/2015/2018: Failure to process negative accidental eccentricity factor in Response Spectrum Analysis  1 - Critical 20.07.11.33 23.00.00.345
A-1121536 EN 1993-1-1:2005 : Failure to perform Bending Check (Clause 6.2.5) and Buckling Check (Equations 6.3.3-661, 662)  1 - Critical 20.07.11.90 23.00.00.345
A-1176400 AISC 360-05/10: Slenderness of Single Angle  2 - High 20.07.11.50 23.00.02.361
A-1199138 AISC 360-16: Incorrect H2-1 at the Heel of an Equal Angle  2 - High 21.00.02.44 23.00.00.345
A-1221514 Wind Load Panel Formation affected by support nodes  1 - Critical 20.07.04.12 24.00.02.354
A-1225794 AS4100-1998 & NZS 3404 -1997: Reference buckling moment for wide flange profiles with unequal flanges  2 - High 20.07.11.90 23.00.02.361
A-1232633 CSA S16-09/14/19: Incorrect Evaluation of Factored Moment Resistance  1 - Critical 20.07.10.64 23.00.02.361
A-1247472 AS4100-1998 : Member moment capacity checks as per Clauses 8.4.2.2 and 8.4.4.1  2 - High 20.07.11.90 23.00.02.361
A-1271381 AS4100-1998 : Physical member design  2 - High 20.07.09.31 24.00.00.577
A-487774 Inclined Joint load using ref Joint  2 - High 20.07.04.12 23.00.02.361
A-487893 Wind load on open structures are incorrectly evaluated on members with beta angles  2 - High 20.07.04.12 23.00.02.361
A-1327542 EN 1993-1-1:2005 : Cl 6.2.2.4 not implemented for I section with Class 3 web and Class 1 or 2 Flange  2 - High 20.07.10.41 23.00.02.361
A-995133 IS 800 2007 (LSD/WSD) : Section classification for Welded Section T Profile  2 - High 20.07.06.23 23.00.02.361
A-1335471 EN 1993-1-1-2005 : Incorrect warping constant values evaluated for Tube and Angle profiles  2 - High 20.07.10.41 24.00.00.577
A-1352814 Time History Analysis: Plate stresses ignore missing mass  2 - High 20.07.10.41 23.00.03.25
A-1350894 AISC 360-05/10/16: Incorrect slenderness for single angles  1 - Critical 20.07.04.12 23.00.03.25
A-807595 NRC 2005/2010: Incorrect assignment of FV parameter  2 - High 21.00.00.57 24.00.00.577
A-1347586 AS4100-1998: Incorrect Section slenderness (λe)  1 - Critical 20.07.07.19 24.00.00.577
A-846868 Incorrect design shear area  2 - High 20.07.04.12 22.12.00.142
A-1419270 AISC 341-16 : Web stiffener parameters  2 - High 21.00.02.30 24.00.00.577
A-1392128 Design code parameters conflicting with other codes  2 - High 20.07.10.41 24.00.00.577
A-1373774 NZS3404-1997: Angle profile slenderness limit (λey)  1 - Critical 21.00.00.57 24.00.00.577
A-1427565 Self-weight distribution for quadrilateral plates  2 - High 20.07.04.12 24.00.00.577
A-1431170 AIJ 2002/2005: Interaction Checks  2 - High 21.03.00.146 24.00.02.354
A-1500567 AISC 360-16: Incorrect H2-1 at the Heel of an Equal Angle  1 - Critical 21.00.02.44 24.00.02.354
A-1482280 AS4100-1998/2020: Shear capacity for circular profiles  2 - High 20.07.07.19 24.00.02.354
A-1543790 AISC 360 & CSA S16: Incorrect minor axis bending capacity for channel profiles  1 - Critical 20.07.08.22 24.00.02.354
A-1547404 AISC 360-05/10/16/22: Incorrect design wall thickness for HSS profiles  1 - Critical 20.07.04.12 24.00.02.354
A-1548004 AISC 360-16/22: Incorrect effective area for a slender round HSS profile  1 - Critical 21.00.01.12 24.00.02.354
A-1559731 AISC 360-16/22: Incorrect calculation of Cb for single angle profiles  1 - Critical 21.00.01.12 24.00.02.354
A-807812 Cold formed design: Russian cold formed pipe profiles  2 - High 20.07.04.12 24.00.02.354
A-488029 Incorrect wind loads on open structures for single angle profiles  1 - Critical 20.07.04.12 24.00.02.354
A-937039 Incorrect wind pressures on open structures  1 - Critical 20.07.04.12 24.00.02.354
A-1100215 Incorrect wind pressures on closed panels  1 - Critical 20.07.04.12 24.00.02.354
A-1398892 Inaccurate wind panel validation  1 - Critical 20.07.07.32 24.00.02.354
A-1568149 Mass overestimation due to improper load placement in dynamic load  1 - Critical 20.07.08.20 25.00.00.539
A-1674513 AISC 360-16/22: Incorrect interaction ratio reported when both H1.1 and H1.3 apply  1 - Critical 21.00.01.12 25.00.00.539
A-1667479 IS800-2007 (LSD): Incorrect λLT Calculation for Wide Flange Profiles  1 - Critical 20.07.06.23 25.00.00.539
A-1674510 AS 4100: Incorrect bi-axial interaction check when axial limit governs (Clause 8.4.5)  1 - Critical 20.07.04.12 25.00.00.539
A-1708628 AISC 360-16/22 : Double Channel Front-to Front specification  2 - High 21.00.01.12 25.00.01.424
A-1708762 Mexican Legacy Database  2 - High 20.07.04.12 25.00.01.424
A-1716778 EN 1993-1-1: Incorrect Section Classification  1 - Critical 20.07.06.23 25.00.01.424
A-1468910 Self weight loading on plates with variable thickness  2 - High 20.07.04.12 25.00.01.424
A-1708447 AISC 360-2016 and 2022: Double Unequal Angles with Short Legs Connected  2 - High 21.00.01.12 25.00.01.424
A-1739410 NRC/NBCC 2010: Incorrect Evaluation of Minimum and Maximum Base Shear for Static Seismic Loading  1 - Critical 21.00.00.57 25.00.01.424
A-1739748 Steady State Analysis: Applied Joint Moments  1 - Critical 21.03.00.146 25.00.01.424
A-1929912 AISC 360-16/22: Incorrect LTB for Tee and Double-Angle  1 - Critical 21.00.01.12 25.00.01.424
A-1988266 Seismic self weight calculation for very short tapered I profiles  2 - High 21.00.02.30 26.00.01.491
A-2038944 Incorrect member design forces using an SRSS combination  1 - Critical 21.00.00.57 26.00.00.340
A-2084603 AS4100 (1998/2020): Incorrect web slenderness limit for Tee profiles  1 - Critical 20.07.04.12 26.00.01.491
A-2094654 AISC 360-16/22: Incorrect default SNUG value for built-up members  1 - Critical 21.00.02.30 26.00.01.491
A-2106652 CSA S16-09/14: Limiting value of Factored Moment Resistance (Mr) as per Clause 13.6(a)(i)  1 - Critical 20.07.10.41 26.00.01.491
A-2009553 Wind Load assignment Combining RANGE and LIST methods  2 - High 20.07.04.12 26.00.01.491
A-2016637 AISC ASD: Incorrect Section Modulus used in design of multiple angle profiles  1 - Critical 20.07.08.22 26.00.01.491
A-2017394 Local deflection checks of models distant from the global origin  2 - High 20.07.04.12 26.00.01.491
A-2024531 Incorrect open-structure wind loading for angle profiles  1 - Critical 20.07.04.12 26.00.01.491
A-2092167 Incorrect processing of floor load within a reference load case  1 - Critical 20.07.08.20 26.00.01.491
A-2011909 EN1993-1-1-2005: Section classification check is skipped  2 - High 20.07.06.23 26.00.01.491
A-2125826 IS 1893 (Part 1) 2016: Incorrect static base shear used for comparison with response spectrum base shear  2 - High 21.03.00.146 26.00.01.491
