| Application | PLAXIS 2D |
| Version | PLAXIS 2D 2023.1 PLAXIS 2D 2023.2 |
| Original Author | Hung Ho Manh - Technical Support Group |
| Date created | 10 October 2023 |
| Date modified | 10 October 2023 |
Excavations (open cut or tunnelling) generally cause ground movement, which could result in damage to adjacent buildings. Therefore, a damage assessment of buildings nearby induced by excavations is needed, especially for shallow foundations. In common practice, the design of an excavation needs to ensure that the surrounding ground movement and wall displacement are within acceptable limits.
Classification of damage (Burland et al., 1997) associated with limiting tensile strain (Boscardin and Cording, 1989) of buildings includes six categories in Table 1:
Table 1: Damage categories (Mair, et al., 1996)
| Categories of damage | Normal degree of severity | Limiting tensile strain (elim,%) |
| 0 | Negligible | 0 - 0.05 |
| 1 | Very slight | 0.05 - 0.075 |
| 2 | Slight | 0.075 - 0.15 |
| 3 | Moderate | 0.15 - 0.3 |
| 4 to 5 | Severe to Very severe | >0.3 |
The tensile strain in a building can be caused by the building bending or shearing deformation and horizontal strain (εh). These strains are calculated based on building deflection (Δ/L) in which the building is considered as an idealized beam with span L and height H, and shown in the following equations (Burland and Wroth, 1974):
where:
εb max/ εd max: tensile strain caused by bending/ shearing, H: height of the building, L: length of the building, E and G are Young’s modulus and shear modulus of the building, I: second moment of area the equivalent beam (i.e. H3/12 in sagging zone and H3/3 in hogging zone), h: furthest distance from the neutral axis to edge of the beam (i.e. H/2 in sagging zone and H in hogging zone).
The maximum deflection (Δ) and the deflection ratio (Δ/L) can be determined based on building deformation shown in Fig. 1 for hogging zone (Δh/Lh) and sagging zone (Δs/Ls).
Fig. 1 Building deformation (Mair, et al., 1996)
The average horizontal strain (εh) is added to the bending or diagonal strain to give the total strain of bending (εbt) and shearing (εdt) shown as follows (Burland, 1995):
Where: v is the Poisson's ratio.
By applying the values of tensile strain limit (εlim) in each damage category, a relationship between deflection ratio (D/L) and horizontal strain (εh) for appropriate values of h, L/H, E/G, v and I of a building is established. The damage criteria diagram corresponding to L/H=1 and E/G=2.6 in the hogging zone is shown in Fig. 2 (Burland, 1995).
Fig. 2. Damage category chart (H/L=1) in hogging mode (Burland, 1995)
Mair et al. (1996) proposed three stages of damage assessment of an adjacent building due to excavations, namely preliminary, second stage and detailed assessments. The first stage is evaluated based on ground surface settlement without building stiffness included (green field site). If the settlement and slope are less than 10 mm and 1/500, respectively, the building is considered to have negligible risk of damage, and no further assessment is necessary. If one of these ground deformations is beyond the limit, the second stage (using green field site) and third stage (building stiffness included) are further evaluated based on deflection ratio (Δ/L) and maximum tensile strain (εbt or εdt). The third stage is carried out if the building in the second stage is classified as being at risk of moderate damage or greater.
The deflection ratio and tensile strain in a numerical model are conveniently extracted if automation scripting is used. A Python script built up to extract these outputs in PLAXIS to evaluate the damage risk of an adjacent building due to an excavation is briefly introduced in the following section.
Once a model has been run (Fig. 3), the Python script for damage assessment can be used. This script is designed to work with PLAXIS Output only. It extracts the footing deformation, including settlement, deflection, and horizontal strain. Two criteria used for the damage assessment comprising of footing deflection ratio and horizontal strain are plotted in a diagram of damage levels (Fig. 4), which is determined based on the building parameters, i.e., E/G and L/H, and a hogging or sagging zone.
Fig. 3. Excavation model
Fig. 4. Damage criteria and footing deformation
It is noted that there are two points of footing deformation (hogging and sagging) in the plot. Depending on the plot type (hogging or sagging), the corresponding point is used for the building risk assessment. Furthermore, it is generally used for shallow foundations.
Extracting footing deformation in PLAXIS 2D and plotting it in a damage chart to evaluate the damage risk of a building.
You will need the following:
To use this Python script:
The script is tested with PLAXIS 2D 2023.1, PLAXIS 2D 2023.2 and Python 3.8.
Copyright (c) Plaxis bv. All rights reserved. Unless explicitly acquired and licensed from Licensor under another license, the contents of this file are subject to the Plaxis Public License ("PPL") Version 1.0, or subsequent versions as allowed by the PPL, and You may not copy or use this file in either source code or executable form, except in compliance with the terms and conditions of the PPL.
All software distributed under the PPL is provided strictly on an "AS IS" basis, WITHOUT WARRANTY OF ANY KIND, EITHER EXPRESS OR IMPLIED, AND LICENSOR HEREBY DISCLAIMS ALL SUCH WARRANTIES, INCLUDING WITHOUT LIMITATION, ANY WARRANTIES OF MERCHANTABILITY, FITNESS FOR A PARTICULAR PURPOSE, QUIET ENJOYMENT, OR NON-INFRINGEMENT. See the PPL for specific language governing rights and limitations under the PPL.