User notification "Pump exceeds the maximum operating point specified for the pump curve"
  Product(s):
WaterGEMS, WaterCAD
  Version(s): All
My pumps are operating at a much higher rate than the design point. How do I fix this?
OR
What does the user notification "Pump exceeds the maximum operating point specified for the pump curve" mean?
The first step to solving this problem starts with understanding how pumps function in the OpenFlows products. You can find that explanation in this wiki.
The second step is to check the pump curves for the pumps that are adding too much flow or head and make sure the curves are correct. If the curves are correct check the head and flow being output by the pump is on the pump curve.
Next, check the demands in your model for the junctions, hydrants, tanks, and the HGL on your reservoirs that are downstream of the pump.  The best way to check your demands on downstream elements is to make a selection set of all those nodes and then open your flextable based on that selection set. There are directions in the article found here that explain how to do this. With the flextable open add the column called "Demand" if it's not already. This article will explain how to do that. Once that column is added you can right click on the column header and choose statistics to see the total sum of the demand and other important information. At this point you can also sort that column by right clicking on it and choosing Sort > Descending because you are likely looking for values in the column that are to high. After doing this you should scan all the demands to make sure they are correct. Note that for the reservoir there is no "demand" column. You should be checking the hydraulic grade in reservoirs to make sure that it is set correctly.
Finally, if you are checking the demands for an EPS simulation you should use the time browser to choose the time step where the pumps are operating higher than the design point and then use the steps above to check the appropriate tables for the demands.
Pumps in the OpenFlows products operate by adding enough head to system to balance the hydraulic grade in the system, namely by overcoming the losses and elevation differences between your upstream and downstream boundary conditions. The head and flow rate is defined on your pump definition curve. In the water products, like WaterGEMS and WaterCAD, the pumps need to also add enough flow to be able to fulfill the demand. The pump operating point is the point where the pump curve intersects the system head curve. See: Understanding System Head Curves in WaterGEMS, WaterCAD, and SewerCAD
This warning message usually indicates that the pump is operating beyond the user-entered pump characteristic curve (pump definition). This will happen when the pump definition is not defined all the way out to zero head. WaterCAD and WaterGEMS will use extrapolation on the pump curve, so that it extends all the way to zero head. The pump can operate past the user entered range if the system conditions warrant it. The pump curve that you see in the system head curve viewer is an extrapolated pump curve.
The warning message may indicate that the real pump may not be able to operate correctly in this condition. Basically, the system conditions are such that the head the pump needs to add is less than the lowest head value in your pump curve.
You can always check the operating point and extrapolated pump curve by right clicking the pump and selecting "Pump Curve".
You should compare the operating point to the actual pump curve that you have defined under Components > Pump Definitions, and not to the system head curve window.
Sometimes you may also get this message if you are using a multiple point pump curve with large gaps between flow values.  If this is the situation you're facing, the issue can usually be resolved by adding one or two flow values with its corresponding head value to make the gaps between consecutive values smaller.
A note on Variable Speed Pumps (VSPs)
Please note that VSPs can still operate in the extrapolated part of the pump curve (and you will see the notification in question). When modeled in parallel, they will not automatically turn on an additional lag pump if the other pumps operate in the extrapolated part of the curve. See below for options.
But I want my force my pump not run run beyond the end of the defined curve!
Ideally you should instead explicitly model exactly how the real system operates, such as controls to turn the pump off if that is what happens in the real system to prevent the pump from operating beyond the curve.
If you really want to forcefully prevent the pumps from operating beyond the last point you defined in the curve, choose "True" for "User Linear Interpolation for Multipoint pumps" (in the Calculation Options), then create a copy of your pump definition, with the type set to "Multiple points". Enter the same curve that you had before, but add an additional row at the end with zero head, and a flow slightly higher than the previous flow. In the pump curve graph seen in the pump curve dialog, you will see the head sharply drop to zero at the end of your curve.
I'm not seeing the "exceeded max operating point" notifications when I should!
This is due to a known issue specifically for multi-point pump curves (reference # 1961626) and is planned to be fixed starting with the version 26.00.01.XX. Contact Technical Support for help.
Pump cannot deliver flow or head user notification