Fire flow analysis at the time of minimum pressure (EPS Fire Flow Analysis Tool)


Product(s): WaterGEMS, WaterCAD
Version(s): 10.00.00.55 and higher
Area: Modeling

 

What it Does

The EPS Fire Flow Analysis tool automates specific fire flow results. It provides a way to run a range of flows on each fire flow node, only at the time of minimum pressure from an EPS, and run the full EPS up to that point.

Benefits

Some regulatory agencies require this type of analysis (eg. Australia).

Applicable Products and Version

The EPS Fire Flow Analysis tool is available for WaterGEMS version 10.00.00.55 and later. It is not currently available for WaterCAD.

But what if I want it to look at a specific time during an EPS, not the time of minimum pressure?

This tool runs fireflow for each node at the time of minimum pressure during an EPS, which is a specific standard requirement for certain regulatory agencies.

This tool does not currently enable you to override this and enter a specific EPS time. If you have a need to do this, you will need to create your own version of this tool using the WaterObjects.NET API (advanced programming experience and a BDN subscription required). Or, manually run each fireflow node using this workflow:

  1. Compute the EPS scenario of interest
  2. Right click on the first fireflow node and choose Hydrant Flow Curve
  3. Select the desired time and compute the hydrant flow curve. This will show you the resulting residual pressure for a range of flow, at that time.
  4. Repeat for each fireflow node and scenario.

Alternatively if you wish to perform a standard automated fireflow analysis, but at a specific time:

  1. Compute the EPS scenario of interest and advance the Time Browser to the desired time.
  2. Note the status of elements such as pumps, tanks and valves
  3. Set up a child scenario with a child initial settings alternative, make that scenario active, then adjust the initial status of each of those elements to be what you observed at the desired time.
  4. Create and use a new Calculation Option in that scenario, set it to fireflow and set it to be an EPS Snapshot, then select the desired time (so it picks up on the demand pattern multiplier at that time)
  5. Compute fireflow and review results.

How to Access the EPS Fire Tool

Starting with WaterGEMS and WaterCAD CONNECT Edition Update 2 (10.02.XX.XX and higher), this tool is now installed with the application. Browse to the installation folder to find the file Haestad.EPSFireFlow.exe to access this tool. If you are using WaterCAD, you will go to the same location, only clicking the WaterCAD folder instead.

If you have an older version, first make sure you are using WaterGEMS or WaterCAD version 10.00.00.55 or greater. Click here to see how to determine the version you are using.

Next, Determine if you are using the product in 32-bit or 64-bit mode. To check, go to: File > Help > About WaterGEMS. The bottom of the dialog will show either 32-bit or 64-bit.

Download:

Version Download Link
10.00.00.50 &
10.00.00.55
Download
10.01.00.72 Download
10.02.00.43 Download
10.02.02.06 Download

 

Install:

1. Download and extract the following .zip file: 

2. Copy the extracted "Haestad.EPSFireFlow.exe" files from installation folder. 

3. Run the "Haestad.EPSFireFlow.exe" file from the x64 subfolder to run the 64-bit version. 

How to Use

The tool is very simple to use and provides minimal options. When running the "Haestad.EPSFireFlow.exe" file the following dialog will appear.

Note: if there is an issue starting the tool then try right-clicking on the executable file and selecting "Run as Administrator". Also ensure that the version of the tool matches the version of WaterGEMS that you have installed (check under File > Help > About).

1. Select the model

Click the Open button to select a WaterCAD or WaterGEMS hydraulic model to use for the analysis.

Once the project is open, there are options that must be specified before calculating the EPS Fire Flow.

2. Select the scenario(s)

a. Click the Scenarios button to display the "EPS Fire Flow Scenario Selection" dialog.

b. Select at least one EPS scenario, and then click OK.

3. Choose a selection set

Choose a selection set from this dropdown list to use for the EPS fire flow analysis. The junctions and hydrants in the chosen selection set will be included in the analysis. Each of these junctions and hydrants will have the fire flows applied (during the time when the pressure is lowest) for each fire flow included in the range.

Note:

4. Specify how fire flows will be applied

In the "Apply Fire Flows By" dropdown, specify if the fire flows will be applied by adding to the baseline demand or if they will replace the baseline demand.

5. Select a range type

Range: This allows a Minimum, Maximum, and Increment to be entered to establish the range of flows that will be tested for each fire flow node in the selection set.

User Defined Flows: This will establish the range of flows that will be tested for each fire flow node in the selection set. When this is selected then flows can be manually added and deleted in a tabular format.

Calculation Steps

To calculate the EPS fire flows click the Compute button to the right of the Open button in the toolbar.

Here are the steps performed by the tool:

  1. Compute each scenario.
  2. Determine the times during the EPS scenarios when the active node in the selection set is at its respective minimum pressure.
  3. Compute a hydrant flow curve for all active nodes in the selection set for the scenarios selected. Each hydrant flow curve will be created at the time each node is at its respective minimum pressure.
  4. Use the hydrant flow curves to find the residual pressures for each of the user-specified fire flow values, for each combination of the specified scenarios, nodes and times.

See: Help Topic "Hydrant Flow Curve Editor"

Data Validation

The data is validated when computing. An error will appear if any of the following are true:

Results

The results are presented in a table once the calculation is successfully completed. If the validation fails, no results are displayed until the issues reported are resolved.

The first three columns are always available showing the scenario label, the fire node label and the time at minimum pressure.

The remaining columns are based on the flow range specified. The hydrant flow curves (created for each combination of scenario, node and time) are used to interpolate the residual pressure for each flow specified in the fire flow range. If the interpolation returns a negative pressure, (N/A) is shown in the table. Otherwise, any pressure greater than zero is displayed.

Units

The units used in the tool are based on the settings of the open project. You can change units by right-clicking the unit next to the minimum, increment and maximum fields on the main dialog and clicking "Units and Formatting". You can change the units of pressure in the results table by right-clicking the column header and clicking "Units and Formatting".

Other Notes

No changes are made to the project opened. When closing the tool or opening a different project, the project that was previously opened (if there was a project opened) is not saved.

Troubleshooting

If the tool crashes with a "...stopped working" message (known to occur in version 24.00.02.20), try these steps:

  1. Open Windows File Explorer and browse to the installation folder
  2. Locate the file named WaterCAD.exe.config (or WaterGEMS.exe.config) and make a copy of it (for example copy and paste it to another folder)
  3. Rename the copy to: Haestad.EPSFireFlow.exe.config
  4. Move it back to the installation folder (so it is in the same folder as Haestad.EPSFireFlow.exe)
  5. Re-run the Haestad.EPSFireFlow.exe and try again.

See Also

EPS (Extended Period Simulation) Fire Flow Analysis

Understanding Automated Fire Flow Results