WaterSight - Preparing WaterGEMS model for real time simulation WaterSight


Product(s): WaterSight
Area: Documentation

 

Creating a live Digital Twin of the system

Direct measurements from SCADA or other telemetry systems together with demand patterns calculated within the application can be used to override and adjust model boundary conditions and with this turning the typical static hydraulic model into a real live digital twin, a real time hydraulic model of the system, and contributing to increase the confidence and accuracy in the model calculated results. The user can now investigate the real-time performance for each asset and use the most updated model to simulate emergency events such as pipe breaks, fires, pump shutdowns and valve closures. 

As previously mentioned, WaterSight allows to:

WaterSight supports upload up to 10 different and independent WaterGEMS models per digital twin.

 

WaterGEMS model setup - General Tips

Take a look at the general tips section included in this article - Numerical Model Administration.

 

WaterGEMS model setup - SCADA Elements and Control Overrides

Recommended:

In order to have the initial conditions imposed to the instant corresponding to the start of the simulation or in order for the user to directly compare modeled data with measure data, it is required that in the WaterGEMS model that is uploaded to WaterSight (under Administration >> Numerical Models):

Note: The SCADA signals should be created and listed but it is not required to have the live connection with the sensors data sources/data bases established in the model that will be uploaded in WaterSight. The connection with the data sources/ data bases is done by the Data Pusher (OpenFlows Onsite Coordinator) or Rest API connection. More information in video below. 

Below an example of the SCADA signals name/tags and units in WaterGEMS (that need to match those defined in the sensor administration page of WaterSight)

Below an example of a SCADA element created in the WaterGEMS model and mapped to the associated model element (in this case tank level).

 

Importing Historical Overrides:

Imported overrides are defined in the WaterGEMS model and allow the user to have the system operate as it did at the time of the specified historical simulation (inferred from the historical scada data). By default, Imported Control Overrides take precedence over 'Regular' Controls. If there is a conflict between a Regular and Imported override, the Imported override will take precedence. If you want the "Regular" Control Override to take precedence, you can increase the priority.

When the calculation option Automatically Import Control Overrides is set to True and the SCADA calculation simulation mode is Historical or Historical (Live Training), pump status and valve status will be imported to Active Control Overrides. First, the existing control overrides are cleared. Then, new control overrides are imported from SCADA data and used in SCADA calculation. When there is conflict between pump (or valve) control and SCADA signal, SCADA signal pump (or valve) status are used in control pump (or valve) status. Only pump and valve statuses within simulation time range are imported.

The following is pump status result comparison with SCADA signal when Automatically Import Control Override is set to false in SCADA simulator Historical calculation. At some calculation time steps, the pump status is different from SCADA signal.

The following is pump status result comparison with SCADA signal when Automatically Import Control Overrides is set to true in SCADA simulator Historical calculation. 

More information about control Overrides can be found here: Importing Historical Control Overrides in WaterGEMS

 

WaterGEMS model setup - Calculation Options

Required/Mandatory:

 

WaterGEMS model setup - Videos

In summary, to run WaterGEMS model in real time in WaterSight it is required to:

  1. Create SCADA signals in the WaterGEMS model, and the tag names need to match those defined in WaterSight
  2. Create SCADA elements and map signals to model elements
  3. Update calculation options

1. Create SCADA signals in the WaterGEMS model (or updating existing tags)

The SCADA signals created need to have the same tag names as the sensor tags defined in WaterSight which match the tags or ID used in the data source (database or API). To add new SCADA signals to the model or to update existent SCADA signals tags (to match tags in WaterSight), the easier method is to use ModelBuilder tool inside WaterGEMS. Video below describes both use cases.

2 and 3. Create SCADA elements, map signals and update calculation options

After SCADA signals are created (with same tags as those in WaterSight) - see video above, the next step is to create SCADA elements and use those to map signals and model elements. And finally update calculation options. Check video below for more detail.

For more information on how to configure SCADA elements in WaterGEMS, you can also take a look at this article: Using the SCADA element

 

WaterGEMS model setup - Water Quality

To consider water quality simulation such as water age, constituent simulation (like chlorine) or water trace, in WaterSight it is required that the uploaded WaterGEMS model is already pre-configured with the water quality parameters and also the SCADA calculation type needs to be set to "Age, Constituent & Trace" (see above). 

For a detailed procedure on how to setup water quality simulations in WaterSight such as a constituent simulation, take a look here - Water Quality Constituent Simulation in WaterSight.

 

Imposing initial conditions to the hydraulic model based on sensors measurements

The sensors measurements that can be used to override the initial conditions of the hydraulic elements are the marked as Yes in the below table. All the other attributes listed in the table, even those that can not be used to override the initial conditions for the hydraulic model, can always be used to compare model results with the real measurement results.

In order to impose initial conditions from sensors into the hydraulic model or to compare model results with measured results it is required that SCADA elements are already created in the WaterGEMS model, associated with a valid SCADA signal and correctly mapped to the model element as mentioned above. 

Table 1 - sensor measurements types that can be associated with hydraulic model elements

Element Type

Attribute

Can be used as Initial Setting for the model runs?

Can be used to compare model results with sensor results?

Reservoir

Hydraulic Grade

Yes

Yes

Junction

Pressure

No

Yes

Hydraulic Grade

No

Yes

Demand

No

Yes

Concentration

Yes

Yes

Pump

Concentration

No

Yes

Flow

No

Yes

Hydraulic Grade (From/To)

No

Yes

Pressure (From/To)

No

Yes

Pump Status

Yes

Yes

Relative Speed Factor

Yes

Yes

Wire Power

No

Yes

Pipe

Flow

No

Yes

Pipe Status

Yes

Yes

PRV/PSV

Concentration

No

Yes

Flow

No

Yes

Hydraulic Grande (From/To)

No

Yes

Pressure (From/To)

No

Yes

Valve Status

Yes

Yes

Hydraulic Grade Setting

Yes

Yes

Pressure setting

Yes

Yes

FCV

Concentration

No

Yes

Flow

No

Yes

Hydraulic Grande (From/To)

No

Yes

Pressure (From/To)

No

Yes

Valve Status

Yes

Yes

Flow Setting

Yes

Yes

TCV

Concentration

No

Yes

Flow

No

Yes

Hydraulic Grande (From/To)

No

Yes

Pressure (From/To)

No

Yes

Valve Status

Yes

Yes

Relative Closure

Yes

Yes

Headloss Coefficient Setting

Yes

Yes

GPV

Concentration

No

Yes

Flow

No

Yes

Hydraulic Grande (From/To)

No

Yes

Pressure (From/To)

No

Yes

Valve Status

Yes

Yes

Tank

Level

Yes*

Yes

Hydraulic Grade

Yes*

Yes

Concentration

No

Yes

Tank Status

No

Yes

 * The tank definition in the model must match the SCADA type. If the SCADA signal is Level, the tank "Operating Ranging Type" should be defined by Level. If HGL, then tank  "Operating Ranging Type" should be defined by Elevation.

 

Initial conditions, based on sensors data (those marked as Yes in the above table), will be always imposed to the instant corresponding to the start of the simulation. The start of the simulation is illustrated below:

Whenever a new simulation is triggered (Now), the simulation start and end time are set by:

  1. Defining a new Now*, which Now rounded down to the previous full hour
  2. The start of the simulation is the Now* - the hindcast period. 
  3. The end of the simulation is Now*+ the forecast period.

Note that when zone demand adjustments, smart meter adjustments, or HGL adjustments are activated in WaterSight (under Admin >> Numerical Models), these adjustments are applied across the entire simulation period rather than being limited to the initial condition at the simulation start time. 

In case the user wants to use in the model runs the initial conditions from SCADA for the Now instant, the user should set an hindcast period of zero. Please note that the sensor values used for the model initial conditions corresponds to the processed 15 minutes time series and not the raw sensor time series. The processed 15 minutes time series already has some clean-up, so this can minimize some outliers being considered for the model runs and affecting all the model results.

Please note that in case sensor results from SCADA or other telemetry systems are not available, the hydraulic model will still run but instead assuming the real measurements for the boundary conditions (real tank levels, real zone flows, real PRV settings, etc) the initial model values defined in the WaterGEMS model will be assumed.

 

Upload WaterGEMS model into WaterSight

After all setups are done it is required to upload the WaterGEMS model into WaterSight. This is done by acceding the Administration > Numerical Models. More information on the model upload process can also be found in the WaterSight Administrator Guide (Numerical Model section). Note that WaterSight supports up to 10 different and independent WaterGEMS models per digital twin.

 

Unassigning Sensor from Model Element

If a sensor is mapped to a model element as boundary condition and starts to transmit bad data, this data can pass to the hydraulic model and affect the accuracy of the model or even lead the hydraulic model runs to fail. The solution in that case is to temporarily unmap this sensor from the model element. This can be done through the WaterSight application by going to Administration >> sensors, and mark that sensor as offline. Once marked as offline, that sensor will have no more data, and after few hours the new hydraulic model runs will not use the measurements from that specific sensor to override model results. 

Once the sensor has good data again, don't forget to return to the administration and remove the offline status, so it can start again to be used by the hydraulic model. 

 

Comparing sensor data with modelled data

As mentioned above, it is also possible to directly compare measured data with modelled data (in case SCADA elements are created and mapped in the WaterGEMS model file, see above). Once sensor elements are configured in the hydraulic model and associated to the model element, then it is possible to directly compare in the same graph the real sensor measurements with the modelled results to check the accuracy of the hydraulic model. It is important to highlight that this comparison can be done for any sensor that is associated with a hydraulic model element - any sensor type that is contained in the table 1 above.

To see the comparison between the modelled and measured data, the simplest workflow is to go to Network Monitoring >> Sensor Overview >> and turn on model results. Model results will be displayed as a blue line in the graphs. 

More detailed information can be found here - Comparing Modelled data with Measured data. 

 

Adjusting demand and HGL patterns in the model for the all simulation period

Furthermore, pattern adjustments can also be automatically applied (and in this case to all period of the simulation) in case demand adjustment option or hydraulic grade line adjustment option are enabled in the Numerical Models administration. 

If the zone demand adjustment option is on, WaterGEMS patterns applied to each node or customer will be automatically adjusted based on the real zones pattern calculated from the real flow measurements. For more information about automatic demand adjustment, please click here.

The HGL adjustment functionality is particularly useful when using hydraulic models of distribution systems in WaterSight that do not cover the transmission line. For more information about HGL pattern adjustment, please click here.

 

Using AMI/Smart meters data in the model runs

Zones with very large industrial demands may be more accurately modelled in terms of temporal distribution of the demands in case AMI (smart meter) data is available . In case AMI data is available for the Large Customers, WaterSight can use that data to automatically update the patterns for those specific customer meters in the model. More information can be found here - Smart Meter Adjustment.

 

Preparing the model for the geolocation of leaks run

WaterSight can pint-point the most likely spots inside the zone where leakage might be by automatically simulating leaks and comparing model results with the real time measurement results (flow and pressure). To understand better how to trigger the geolocation of leaks run and also how to make sure the model is ready for the leak geolocation, take a look at this article - Geolocation of Leaks.

 

Why model data does not match sensor values for the boundary elements?

In case it is noted that the model values in WaterSight do not match the sensor values for the boundary elements (for example tank levels, PRV settings) please make sure that the units defined for the SCADA signals in the uploaded WaterGEMS model matches the units defined for the sensors in the WaterSight in the Admin >> sensors and are the same as in the database. More information here - Why Model data does not match Sensor values?

 

Fig 1 - Model value at blue does not match sensor measurements (black line) for the PRV boundary element due to mismatch of units defined in the hydraulic model and in the sensor configuration template

 

See Also

Numerical Model Administration

Automatic Demand Adjustment

Automatic Hydraulic Grade Adjustment

Using AMI/Smart meter for model runs

Why Model Runs are failing?

Why Model data does not match Sensor values?

Error uploading GIS shapefiles or hydraulic model