Modeling positive displacement pumps in HAMMER


  Applies To     
  Product(s): HAMMER  
  Version(s): 08.11.XX.XX and higher  
  Area:  Modeling  

Problem

How do I model a positive displacement pump (such as a screw pump, lobe pump, sliding vane pump or progressive cavity pump) for a transient simulation in HAMMER?

Background

HAMMER cannot accurately model a positive displacement pump using the pump element, as the pump element represents a centrifugal pump. Positive displacement pump characteristics are completely different from those used for four-quadrant pump curves used in HAMMER for pumps.

However, it is possible to approximate a positive displacement pump, using a Periodic Head-Flow element.

Solution

First, you would need to externally determine the flow that would occur out of the pump and compile a table of flow versus time. Then you would use two "periodic head-flow" elements in the model, one representing the suction side and one for the discharge side, with a gap between, as shown below.

In the Properties display for the Periodic Head-Flow elements, you would set the attribute "Transient Parameter" to Flow. For "Sinusoidal?", choose False.

This will enable you to define the Flow Pattern table for flow versus time. The tables for each will need to be identical, except that the values for flow. On the suction side, the flow values will be positive (outflow). On the discharge side, they will be negative, to represent inflow. This way, you can approximate the correct flow rates and let the head behave as it should based on the system conditions.

If for example your PD pump is discharging against a valve that closes, you will need to ensure that the Periodic head-flow element accounts for the reduction in flow that occurs as the downstream valve closes. Otherwise if your periodic head-flow element continues trying to force an inflow against a closed valve with no other way for the water to exit, you will see a continuous pressure rise. HAMMER will not know to automatically stop the inflow.

A note on profiles: Note that you would need to create two profiles, one for the portion of the network upstream of the pump (from the reservoir to the upstream periodic flow element), and a second one for the downstream portion (from the second periodic flow to the downstream end). Typically you would not see significant transient effects on the suction side, but looking at a second profile of that single pipe will enable you to check this.

See Also

Help Documentation section: "Positive Displacement Pumps"

Changing or forcing a pattern of hydraulic grade or flow during a transient simulation