Product: | STAAD.Pro | ||
First Affected Version: | 20.07.11.33 | ||
Found in Version: | 22.04.00.40 | ||
Fixed and Released in Version: | |||
Area: | Steel Design as per CSA S16-09/14 | ||
Issue #: | 1093383 |
Bending capacities for Single Angles designed as per CSA S16-09 or CSA S16-14 are being calculated incorrectly by STAAD.Pro. This error affects flexural capacity calculation for both equal and unequal angles.The CSA S16-09 and S16-14 specifications, does not provide specific guidelines on the determination of the bending capacity of single-angle sections. In absence of such guidelines, STAAD.Pro uses corresponding expressions from Clause No. F10.2 of the AISC 360-05 (for CSA S16-09) and AISC 360-10 (for CSA S16-14) codes, for the evaluation of the bending capacity of single angle sections. However due to a coding error, the expression was improperly implemented in the program, due to which the bending capacity was being over-estimated leading to an unconservative design of single angle sections.
Workaround
No workaround is available as of now for this defect.
The defect is being addressed and a fix will be available in the upcoming STAAD.Pro CONNECT Edition V22 Update 5, scheduled to be released during the fall of 2020.