List of critical and high severity defects identified in STAAD.Pro V22 build 22.09.00.115
Issue ID | Title | Severity | 1st affected Build | Fixed in Build |
A-487670 | Incorrect base shear being generated as per Equivalent Lateral Force Method using IBC 2018 | 2 - High | 22.02.00.26 | 22.10.00.153 |
A-524650 | Member section displacement results do not account for lateral releases on members | 2 - High | 20.07.04.12 | Known Issue |
A-772936 | 1893 2015-P4 : Response Spectrum load case in Y direction | 2 - High | 22.08.00.175 | 22.10.00.153 |
A-813848 | Unbraced length : UNF and UNL Parameters | 2 - High | 20.07.08.32 | 22.10.00.153 |
A-817499 | EN 1993-1-1:2005 : LEG parameter for single angle profiles | 2 - High | 20.07.07.32 | 22.11.00.156 |
A-852094 | AISC 360-16 : FY and FU not considered from assigned material | 2 - High | 21.00.02.44 | 22.10.00.180 |
A-852547 | AS 4100 1998 : MAIN and TMAIN Parameters | 2 - High | 22.06.00.138 | 22.11.00.156 |
A-865805 | Incorrect ELFP Torsional Moment : Optional Load Factor Multiplication | 2 - High | 22.01.00.39 | 22.10.00.180 |
A-865842 | AISC 341-16 : Incorrect Seismic Classification for Custom Steel | 2 - High | 22.01.00.39 | 22.10.00.180 |
A-907678 | Direct Analysis : Default Steel Yield Strength | 2 - High | 22.07.00.160 | 22.12.00.142 |
A-935629 | AISC 360-16: SGR parameter | 2 - High | 21.00.02.44 | 22.12.00.142 |
A-969825 | AISC 360-10/05 : Combined flexure and tension | 2 - High | 20.07.11.50 | 22.12.00.142 |
A-973697 | AS4100-1998 : Moment modification factor | 2 - High | 20.07.11.90 | 23.00.00.345 |
A-907508 | Failure to include additional eccentricity moment for single angle profiles under compression as per AISC 360-16 clause E5 | 1 - Critical | 22.09.00.115 | 22.12.00.142 |
A-1003677 | NZS-3404-1997 : Physical member design | 2 - High | 21.00.00.57 | 23.00.00.345 |
A-1005695 | NZS-3404-1997 : Analytical Member Design | 2 - High | 21.00.00.57 | 23.00.00.345 |
A-1015058 | AISI 2016 : Deflection checks | 2 - High | 22.04.00.40 | 23.00.00.345 |
A-993314 | CSA S16-09/14/19: Incorrect calculation of Shear Buckling resistance for Pipe members | 2 - High | 22.08.00.175 | 23.00.00.345 |
A-1032348 | AISC 360-16 and BS5950 Pt 1 : Incorrect shear capacity parallel to the flanges for Double Channel profiles | 2 - High | 21.00.02.30 | 23.00.00.345 |
A-999611 | Incorrect Time History analysis results with a Harmonic Ground motion | 2 - High | 20.07.04.12 | 22.12.00.142 |
A-1037816 | CSA S16-09/14/19 ignores user provided shear areas for UPT ISECTION and UPT WIDE FLANGE profiles | 1 - Critical | 22.08.00.175 | 23.00.00.345 |
A-996557 | IS800:1984: Properties determined by incorrect CG position | 2 - High | 22.05.00.131 | 23.00.00.345 |
A-1073141 | IBC 2012/2015/2018: Failure to process negative accidental eccentricity factor in Response Spectrum Analysis | 1 - Critical | 20.07.11.33 | 23.00.00.345 |
A-1121536 | EN 1993-1-1:2005 : Failure to perform Bending Check (Clause 6.2.5) and Buckling Check (Equations 6.3.3-661, 662) | 1 - Critical | 20.07.11.90 | 23.00.00.345 |
A-1176400 | AISC 360-05/10: Slenderness of Single Angle | 2 - High | 20.07.11.50 | 23.00.02.361 |
A-1199138 | AISC 360-16: Incorrect H2-1 at the Heel of an Equal Angle | 2 - High | 21.00.02.44 | 23.00.00.345 |
A-1213593 | CSA S16-09/14/19 : Failure to account for effective length factors when calculating compressive resistance Cr | 2 - High | 22.08.00.175 | 23.00.02.361 |
A-1221514 | Wind Load Panel Formation affected by support nodes | 2 - High | 20.07.04.12 | Known Issue |
A-1225794 | AS4100-1998 & NZS 3404 -1997: Reference buckling moment for wide flange profiles with unequal flanges | 2 - High | 20.07.11.90 | 23.00.02.361 |
A-1232633 | CSA S16-09/14/19: Incorrect Evaluation of Factored Moment Resistance | 1 - Critical | 20.07.10.64 | 23.00.02.361 |
A-1238499 | IS456-2000 : Check for maximum stirrup spacing as per Cl 26.5.1.5 | 2 - High | 22.07.00.160 | 23.00.02.361 |
A-1247472 | AS4100-1998 : Member moment capacity checks as per Clauses 8.4.2.2 and 8.4.4.1 | 2 - High | 20.07.11.90 | Known Issue |
A-1271381 | AS4100-1998 : Physical member design | 2 - High | 20.07.09.31 | Known Issue |
A-487774 | Inclined Joint load using ref Joint | 2 - High | 20.07.04.12 | 23.00.02.361 |
A-487893 | Wind load on open structures are incorrectly evaluated on members with beta angles | 2 - High | 20.07.04.12 | 23.00.02.361 |
A-1327542 | EN 1993-1-1:2005 : Cl 6.2.2.4 not implemented for I section with Class 3 web and Class 1 or 2 Flange | 2 - High | 20.07.10.41 | 23.00.02.361 |
A-995133 | IS 800 2007 (LSD/WSD) : Section classification for Welded Section T Profile | 2 - High | 20.07.06.23 | 23.00.02.361 |
A-1335471 | EN 1993-1-1-2005 : Incorrect warping constant values evaluated for Tube and Angle profiles | 2 - High | 20.07.10.41 | Known Issue |
A-1352814 | Time History Analysis: Plate stresses ignore missing mass | 2 - High | 20.07.10.41 | 23.00.03.25 |
A-1350894 | AISC 360-05/10/16: Incorrect slenderness for single angles | 1 - Critical | 20.07.04.12 | 23.00.03.25 |
A-807595 | NRC 2005/2010: Incorrect assignment of FV parameter | 2 - High | 21.00.00.57 | Known Issue |
A-1347586 | AS4100-1998: Incorrect Section slenderness (λe) | 1 - Critical | 20.07.07.19 | Known Issue |
A-846868 | Incorrect design shear area | 2 - High | 20.07.04.12 | 22.12.00.142 |